Advant Controller 410 and 450 - Two Profibus-DP devices CI541V1 on the same carrier module
Problem:Solution
A description of this resolution:
"Advant Controller 410 and 450 - Two Profibus-DP devices CI541V1 on the same carrier module" resolves the following:
A description of this resolution:
- See Workaround and Correction
Workaround
The problem will disappear if only one CI541V1 is placed on each carrier module.
Correction
The error will be corrected in a revision of the products, scheduled to be available by end of August 1999.
[ref SR9074 VASMASOITA0088 ]
"Advant Controller 410 and 450 - Two Profibus-DP devices CI541V1 on the same carrier module" resolves the following:
- Two Profibus-DP devices CI541V1 on the same carrier module
If two CI541V1 are used on the same carrier module the carrier module memory can sometimes be disabled and cause a bus error when the CI541V1 is accessed. This causes the two CI541V1 on the carrier module to restart. The Profibus-DP connected to these two CI541V1 will also restart.
Product concerned
Advant Controller 410*1.4/0
Advant Controller 450*2.1/a a = 0,1,2,3
Advant Controller 450*2.2/0
Software concerned
Advant Controller 410
QC01-BAS11*10.0/0
Advant Controller 450
QC07-BAS41*2.0/b b = 0,1,2
QC07-BAS41*3.0/0