Three-position controller with position feedback signal
Problem:Solution
A description of this resolution:
"Three-position controller with position feedback signal" resolves the following:
The underlying cause is:
A description of this resolution:
- Corrective handling
Up to V8.0G three-position output utilize without position feedback signal (disadvantage: no Y-indication) or utilize Pseudo-Splitrange with the following constraints:
- enter both outputs at the same PAR 03,
- select the same parameters for Y1 and Y2,
- enter SP1 and SP2 differently: SP1=100%, SP2=0%.
"Three-position controller with position feedback signal" resolves the following:
- Loop control
If a three-position controller with position feedback signal in the setting mode HAND small Y-adjustments (key +) are carried out, this can be done with false direction or with false switch-on time (TEU).
Constraints:
- Three-position controller with only 1 output. Three-position output with position feedback signal and small switch-on time (TEU approx. 10-100ms). The problem appears up to V8.0G and is at V8.0H eliminated.
The underlying cause is:
- Inaccuracy of the feedback with the small TEU