Answer question
Udating of dataset values in 61850 OPC Server of 800xA with BRCB and Integrity period triggerI ahve
Hello,
I have one problem with the 61850 OPC Server of 800xA and my IEDs. I have 3 report control blocks. Tow of them are triggered by data change or quality change. The third is reported by integrity period or quality change. The integrity period is 3000 ms. I see the report information counter increase with that rate when I use the online tool of the CET, but the value of the analogic measures included in the corresponidng dataset are not uptdated with that rate. The values that I want to see are the instCval and instMag, then I suppose that these values have to been updated with the same rate. In the online of the rcb I can see the entryID and sequence number increasing each 3 seconds. I have not set the seq number and entryID optionals fields to true. If I refresh from the online tool of the CET the values are automatically refreshed. Why my values are not updated correctly.