800F M_ANA analog block rs the hysteresis value is a percentage of the hysteresis value
It appears this number is a percentage of the alarm setpoint value and not the range of the analog. For example a 0-100% analog with a low alarm at 10% and a hysteresis of 5% would mean the hysteresis is actually 5% of 10 (.5) and not 5% of 100 (5). I find this to be very odd, usually hysteresis oe deadband is a percentage of the analog range. Can this be changed or is this fixed in 800F?