Issue :
When an Analogue Input module is removed then , The values of the channel of that module gets freeze. Even after replacing the Faulty Analogue module with a new module, There will be no change in the condition.
Work around :
CI840A module is toggled from Primary --> Secondary and Secondary ---> Primary. After that only the value gets normalised.