Advant Controller 410/450 and CI532V03 (MVI - Siemens 3964(R)) - Data transfer may stop if more than one dataMS per command is requested
Problem:Solution
A description of this resolution:
"Advant Controller 410/450 and CI532V03 (MVI - Siemens 3964(R)) - Data transfer may stop if more than one dataMS per command is requested" resolves the following:
A description of this resolution:
- The error will be corrected in next revision of MVI - Siemens 3964(R) 1.0.
Possibility to circumvent the problem
Do not request more than one dataMS (MVI dataset)per command, which means 24 registers or less per command depending on start address.
This means that ‘number of values’ defined as REF3 in the Command MS may not exceed 24.
[ref SR6019 VASMASOITA0799 ]
"Advant Controller 410/450 and CI532V03 (MVI - Siemens 3964(R)) - Data transfer may stop if more than one dataMS per command is requested" resolves the following:
- Advant Controller 410/450 and CI532V03 (MVI - Siemens 3964(R)) - Data transfer may stop if more than one dataMS per command is requested
The data transfer can stop without error indications. The communication has to be manually restarted by changing the SERVICE terminal in the database element CI532.
Product Concerned
Advant Controller 410
Advant Controller 450
Hardware Unit concerned
CI532V03 (MVI - Siemens 3964(R)), 3BSE003828R1 PR:F and earlier.
- Article imported from the previous version of KnowledgeBank