800xA Multi system Integration problem.
Hii... Today in the morning after making some changes in the Remote Server, when i tried to upload from one of the Engineering Station I faced the following error: "E_AFW_AOM_ASPECT_NOT_FOUND".To sort out this i re-configured the both Control & Functional Structures. Even after then i couldn't able to come out of the problem. I clicked on the option "Clean" and re-assigned the CS & FS, but no improvement and the same error.As soon as I clicked the "Clean" the options "Cen", "Man","Loc","Auto","Manual" & "E1" were replaced with %NLS% in the faceplate of the complete plant, having no other option I deleted the remote access client from the Service Structure and restarted all the workplaces. Then I found the faceplates are fine now.
Now when I'm trying to again connect the remote access client from Aspect Server, the Service Provider is not coming into service mode, I have selected the Node as CS1, the current status is showing as error.
The fault error is E_AFW_CONSYS_PROTOCOL_NOT_FOUND
Help me out from this problem
Answers
The error E_AFW_CONSYS_PROTOCOL_NOT_FOUND may be due to missing protocols used to communicate between the Remote Access Server and Remote Access Client. Or may be due to some missing dll's in the Remote Access Server/Client side. Try to Re-install the 800xA to correct the problem. Hope it helps you.
You should report this problem to your support contact. They should be able to help out.
Anders Hanberg
Product Manager System 800xA Operations