Browse button is not visible, In Signal Configuration of Compact HMI 800 5.1. How to make it visible?
I am trying to connect the signals to the variable, but in the Control Structure\Signal Configration\ Connected option browse option is not visible.
Any solution for this ?
Voted best answer
One of the reason could be that you are trying to browse in the protocol "Internal driver". You can see this in "Control Structure\plc controller type\plc controller configuration ".
To resolve this, create a new plc controller type with "plcOpcclient" protocol. then you should be able to browse.
regards