How to make the status of OPC Server for AC800M as Running?
In OPC Server for AC 800M , can't able to connect to the controller and status in not running.
How to make the status of OPC Server for AC800M as Running?
Please give the solution for this. screenshot is attached
Answers
As per your description of OPC Server Status "Not Running", the possible reason could be that "AC800MC_OPCService" Not running.
Goto Windows Services and Run the "AC800MC_OPCService" Service.
regards,
There are Few things that you can check
1) Go to windows Services
2) ABB MMS Server Services must be running, If MMS Service is OK..Then Check ABB OPCserver for AC800M, If it is stopped.. please start it... if Failed to start due to credentails... go to properties>>Log on> select "This Account">>> Put service acoount with Password and restart OP Server service.
Add new comment