hart device manegement trs error
I have configured HART for 3 controllers out of 5. I am getting this error in 2 controllers.
Error Code: TRS error-1. Tool routing is also enabled in both the controllers. Please help me in sloving this issues.
Answers
Hi
Can you please enble Tool Routing under Controller Settings as shown below.
regards
Poorna
Check that Property management aspect of each module in chain CI854->CI840->AI815 shows correct values of IP address and module address.
I doubt if IP address value in CI854 property management is correct. Is it showing 0.0.0.0 ?
1. try moving CI854 from its position to another one and bring it back to original position. Do this is in Control builder. If that does not work delete CI854 and create again. But be careful as it deletes everything.
2. Or Make your user role to Software developer. Go to Property management aspect of CI854 and double click on CEX-Address and change the value.
Change back user role to original.
If plant is in operation option 1 above is out of question.
You could try option 2 without any impacts.
Also there is another longway of correcting the issue is to run FFBMerge tool in C:\program files\....\Fieldbus Builder\bin. This tool will correct all such issues in one go but you would need to request the tool's password from ABB Support.
by sharath.1991 Rank: 2071 on 9/1/2014 3:02:25 AM | Like (0) | Report
Its already enabled.but still trs error -1 is there.