Server capacity 6.0-3
Hello All,
In one of my project we are sizing the server requirements. The system design is for 800xA SV 6.0-3 with AC800M and AC800M HI controllers. All the below listed functions will be part of one physical server. The system configuration is as below:
1) Domain Controller
2) Aspect Server
3) Connectivity Server (one AC800M Connect and one PLC Connect)
4) FF-OPC server
Tag count:
1) Hardwired tag objects approx. 2000
2) Serial tag objects approx. 5000
3) Graphics approx. 200
Can someone guide if one server (redundant) is sufficient to handle all the above defined configuration?
From manual "3BSE041434-600 A" I was not able to conclude if the above configuration can be handled by one physical server.
Answers
Should be OK in one computer.
For ease of administration I recommend splitting domain controller from 800xA servers. This doubles the hardware use, but could be limited to Windows licenses if hardware is virtualized.
ESXihost1
- DC1
- ASCS1
ESXihost2
- DC2
- ASCS2
Add new comment