ACS800 480VAC 500HP Motor - Faulting on OverFreq (7123) for no reason
Belt conveyor application, using DTC control mode, Parameter 20.01 set at 0 RPM and 20.02 set at 2000 RPM.
Motor running at 1695 RPM, constant speed and trends show no speed changes when it faults on OVERFREQ (7123).
Drive has been replaced as well as RDCU module.
Answers
Is it your belt conveyor running downside? In case yes, it most probably needs brake chopper and resistors. From the manual:
Check adequacy of motor braking torque.
Check applicability of torque control.
Check need for a brake chopper and
resistor(s)
During operation, check:
01.07 DC BUS VOLTAGE V
01.05 TORQUE
Kstoilov is right, in addition to what has already just been indicated, how long has the drive been working with the parameters you've indicated?
If the drive was working for a long time but the failure appeared, you can not rule out any other kind of internal drive problem, for example in the capacitors, the effect of which could be a 7123 failure. You replaced it with the same drive and with the same parameters?

by mvalente Rank: 5704 on 8/5/2017 7:32:26 AM | Like (0) | Report
Drive system running for over 5 years without any problems.
Drive has been replaced and used same parameters.
ID Run was done using reduced mode. Would ID Run cause this kind of issue?
Do I need to disconnect the motor from the conveyor and run a full ID Run?
by mvalente Rank: 5704 on 8/5/2017 7:41:19 AM | Like (0) | Report
Fault logged by NETA-21:
by mvalente Rank: 5704 on 8/5/2017 7:41:32 AM | Like (0) | Report
name: Datalog
value_columns: ["01_03_FREQUENCY","01_04_CURRENT","01_05_TORQUE","03_04_LIMIT WORD 1"]
device: ddcs_01_datalogger2
device_timestamp: 15:19:08.6000
timestamp: 2017-08-05T09:42:26+00:00
triggered_by: fault
pre_trigger_ms: 690.0
time_step_ms: 3.0
trigger_conditions: fault, external
trigger_variable: 104.01
trigger_level: 90.000
trigger_hysteresis: 0.000
pre_trigger_count: 230
×tamp;01_03_FREQUENCY;01_04_CURRENT;01_05_TORQUE;03_04_LIMIT WORD 1;&event_name
0015:19:07.9100;56.681;275.837;43.079;0;
0015:19:07.9130;56.680;275.407;43.137;0;
0015:19:07.9160;56.679;275.498;43.191;0;
0015:19:07.9190;56.679;275.782;43.246;0;
0015:19:07.9220;56.677;275.988;43.298;0;
0015:19:07.9250;56.677;276.038;43.347;0;
0015:19:07.9280;56.676;274.541;43.391;0;
0015:19:07.9310;56.675;271.791;43.426;0;
0015:19:07.9340;56.674;273.135;43.464;0;
0015:19:07.9370;56.673;272.786;43.496;0;
0015:19:07.9400;56.672;273.567;43.528;0;
0015:19:07.9430;56.671;275.142;43.560;0;
0015:19:07.9460;56.672;274.708;43.590;0;
0015:19:07.9490;56.672;273.179;43.615;0;
0015:19:07.9520;56.672;271.496;43.632;0;
0015:19:07.9550;56.672;271.144;43.646;0;
0015:19:07.9580;56.672;271.515;43.659;0;
0015:19:07.9610;56.673;269.758;43.662;0;
0015:19:07.9640;56.674;268.892;43.660;0;
0015:19:07.9670;56.675;267.063;43.653;0;
0015:19:07.9700;56.676;266.135;43.641;0;
0015:19:07.9730;56.676;266.173;43.625;0;
0015:19:07.9760;56.677;266.294;43.606;0;
0015:19:07.9790;56.679;265.735;43.583;0;
0015:19:07.9820;56.680;262.996;43.548;0;
0015:19:07.9850;56.681;263.129;43.514;0;
0015:19:07.9880;56.681;263.716;43.477;0;
0015:19:07.9910;56.683;265.003;43.446;0;
0015:19:07.9940;56.685;264.966;43.413;0;
0015:19:07.9970;56.687;263.412;43.372;0;
0015:19:08.0000;56.688;261.691;43.327;0;
0015:19:08.0030;56.689;260.925;43.279;0;
0015:19:08.0060;56.690;260.341;43.231;0;
0015:19:08.0090;56.691;260.012;43.183;0;
0015:19:08.0120;56.692;261.191;43.138;0;
0015:19:08.0150;56.694;261.697;43.094;0;
0015:19:08.0180;56.695;260.117;43.047;0;
0015:19:08.0210;56.695;260.141;43.001;0;
0015:19:08.0240;56.697;260.133;42.959;0;
0015:19:08.0270;56.698;260.383;42.913;0;
0015:19:08.0300;56.700;260.636;42.868;0;
0015:19:08.0330;56.700;261.181;42.824;0;
0015:19:08.0360;56.701;261.099;42.784;0;
0015:19:08.0390;56.703;260.656;42.744;0;
0015:19:08.0420;56.704;259.589;42.699;0;
0015:19:08.0450;56.706;260.004;42.658;0;
0015:19:08.0480;56.707;259.080;42.615;0;
0015:19:08.0510;56.707;258.891;42.572;0;
0015:19:08.0540;56.709;259.084;42.531;0;
0015:19:08.0570;56.709;259.220;42.491;0;
0015:19:08.0600;56.709;259.369;42.455;0;
0015:19:08.0630;56.709;260.623;42.422;0;
0015:19:08.0660;56.711;261.956;42.395;0;
0015:19:08.0690;56.713;262.221;42.369;0;
0015:19:08.0720;56.714;261.350;42.339;0;
0015:19:08.0750;56.715;259.198;42.304;0;
0015:19:08.0780;56.715;259.216;42.273;0;
0015:19:08.0810;56.715;259.851;42.243;0;
0015:19:08.0840;56.716;261.475;42.219;0;
0015:19:08.0870;56.717;261.064;42.194;0;
0015:19:08.0900;56.718;260.407;42.170;0;
0015:19:08.0930;56.717;260.342;42.145;0;
0015:19:08.0960;56.718;261.028;42.126;0;
0015:19:08.0990;56.718;261.568;42.109;0;
0015:19:08.1020;56.718;261.702;42.095;0;
0015:19:08.1050;56.718;261.174;42.083;0;
0015:19:08.1080;56.719;261.020;42.073;0;
0015:19:08.1110;56.718;260.651;42.062;0;
0015:19:08.1140;56.718;262.309;42.055;0;
0015:19:08.1170;56.718;264.372;42.058;0;
0015:19:08.1200;56.719;263.748;42.055;0;
0015:19:08.1230;56.719;263.535;42.056;0;
0015:19:08.1260;56.719;263.163;42.055;0;
0015:19:08.1290;56.718;263.004;42.052;0;
0015:19:08.1320;56.718;264.606;42.054;0;
0015:19:08.1350;56.719;265.035;42.059;0;
0015:19:08.1380;56.720;263.857;42.059;0;
0015:19:08.1410;56.721;262.668;42.060;0;
0015:19:08.1440;56.721;261.194;42.057;0;
0015:19:08.1470;56.719;260.691;42.051;0;
0015:19:08.1500;56.718;262.036;42.052;0;
0015:19:08.1530;56.718;264.441;42.059;0;
0015:19:08.1560;56.719;265.413;42.066;0;
0015:19:08.1590;56.719;265.549;42.074;0;
0015:19:08.1620;56.720;265.142;42.081;0;
0015:19:08.1650;56.719;263.537;42.081;0;
0015:19:08.1680;56.719;264.075;42.086;0;
0015:19:08.1710;56.719;263.744;42.090;0;
0015:19:08.1740;56.719;263.878;42.089;0;
0015:19:08.1770;56.719;263.826;42.092;0;
0015:19:08.1800;56.719;263.794;42.092;0;
0015:19:08.1830;56.719;263.853;42.092;0;
0015:19:08.1860;56.719;263.802;42.095;0;
0015:19:08.1890;56.718;264.076;42.099;0;
0015:19:08.1920;56.718;263.829;42.103;0;
0015:19:08.1950;56.718;263.722;42.110;0;
0015:19:08.1980;56.717;264.437;42.118;0;
0015:19:08.2010;56.717;265.109;42.127;0;
0015:19:08.2040;56.717;265.906;42.140;0;
0015:19:08.2070;56.717;265.930;42.151;0;
0015:19:08.2100;56.719;265.023;42.156;0;
0015:19:08.2130;56.719;263.265;42.157;0;
0015:19:08.2160;56.718;262.999;42.156;0;
0015:19:08.2190;56.717;263.149;42.154;0;
0015:19:08.2220;56.717;263.918;42.160;0;
0015:19:08.2250;56.717;263.914;42.163;0;
0015:19:08.2280;56.717;264.168;42.169;0;
0015:19:08.2310;56.717;264.037;42.174;0;
0015:19:08.2340;56.716;264.155;42.178;0;
0015:19:08.2370;56.716;264.834;42.187;0;
0015:19:08.2400;56.716;265.965;42.196;0;
0015:19:08.2430;56.717;267.051;42.205;0;
0015:19:08.2460;56.718;266.268;42.212;0;
0015:19:08.2490;56.717;264.933;42.215;0;
0015:19:08.2520;56.716;263.728;42.216;0;
0015:19:08.2550;56.715;265.330;42.220;0;
0015:19:08.2580;56.714;267.169;42.232;0;
0015:19:08.2610;56.714;267.370;42.245;0;
0015:19:08.2640;56.713;266.338;42.257;0;
0015:19:08.2670;56.712;267.060;42.275;0;
0015:19:08.2700;56.710;267.480;42.294;0;
0015:19:08.2730;56.709;268.867;42.320;0;
0015:19:08.2760;56.708;270.129;42.349;0;
0015:19:08.2790;56.707;271.211;42.380;0;
0015:19:08.2820;56.707;270.403;42.408;0;
0015:19:08.2850;56.705;270.232;42.439;0;
0015:19:08.2880;56.703;270.696;42.474;0;
0015:19:08.2910;56.702;270.705;42.511;0;
0015:19:08.2940;56.700;272.314;42.553;0;
0015:19:08.2970;56.699;273.746;42.592;0;
0015:19:08.3000;56.699;273.282;42.635;0;
0015:19:08.3030;56.698;271.869;42.675;0;
0015:19:08.3060;56.697;271.543;42.713;0;
0015:19:08.3090;56.696;271.964;42.752;0;
0015:19:08.3120;56.695;271.480;42.788;0;
0015:19:08.3150;56.695;270.473;42.821;0;
0015:19:08.3180;56.694;270.397;42.854;0;
0015:19:08.3210;56.693;269.514;42.882;0;
0015:19:08.3240;56.692;269.525;42.910;0;
0015:19:08.3270;56.691;270.533;42.939;0;
0015:19:08.3300;56.691;271.644;42.970;0;
0015:19:08.3330;56.692;270.337;42.996;0;
0015:19:08.3360;56.691;268.615;43.015;0;
0015:19:08.3390;56.691;268.322;43.033;0;
0015:19:08.3420;56.690;268.206;43.049;0;
0015:19:08.3450;56.691;268.587;43.062;0;
0015:19:08.3480;56.692;268.464;43.070;0;
0015:19:08.3510;56.693;267.124;43.071;0;
0015:19:08.3540;56.693;264.939;43.067;0;
0015:19:08.3570;56.694;264.078;43.058;0;
0015:19:08.3600;56.693;264.268;43.047;0;
0015:19:08.3630;56.694;265.361;43.035;0;
0015:19:08.3660;56.695;265.191;43.021;0;
0015:19:08.3690;56.697;264.924;43.004;0;
0015:19:08.3720;56.698;263.020;42.981;0;
0015:19:08.3750;56.700;261.219;42.952;0;
0015:19:08.3780;56.701;260.375;42.917;0;
0015:19:08.3810;56.702;259.985;42.881;0;
0015:19:08.3840;56.703;259.729;42.840;0;
0015:19:08.3870;56.705;260.193;42.801;0;
0015:19:08.3900;56.705;259.214;42.759;0;
0015:19:08.3930;56.705;258.891;42.715;0;
0015:19:08.3960;56.706;261.005;42.677;0;
0015:19:08.3990;56.707;262.419;42.644;0;
0015:19:08.4020;56.707;263.056;42.611;0;
0015:19:08.4050;56.709;262.511;42.581;0;
0015:19:08.4080;56.710;261.817;42.553;0;
0015:19:08.4110;56.711;260.240;42.521;0;
0015:19:08.4140;56.711;260.304;42.492;0;
0015:19:08.4170;56.711;261.193;42.462;0;
0015:19:08.4200;56.712;261.959;42.433;0;
0015:19:08.4230;56.711;261.679;42.408;0;
0015:19:08.4260;56.711;261.763;42.388;0;
0015:19:08.4290;56.712;262.623;42.368;0;
0015:19:08.4320;56.712;264.466;42.356;0;
0015:19:08.4350;56.713;264.608;42.344;0;
0015:19:08.4380;56.714;263.583;42.331;0;
0015:19:08.4410;56.714;262.182;42.316;0;
0015:19:08.4440;56.714;261.669;42.302;0;
0015:19:08.4470;56.713;261.840;42.287;0;
0015:19:08.4500;56.713;263.779;42.280;0;
0015:19:08.4530;56.713;264.422;42.275;0;
0015:19:08.4560;56.714;264.390;42.270;0;
0015:19:08.4590;56.714;262.974;42.265;0;
0015:19:08.4620;56.714;262.002;42.259;0;
0015:19:08.4650;56.714;262.517;42.254;0;
0015:19:08.4680;56.715;263.925;42.248;0;
0015:19:08.4710;56.715;263.302;42.239;0;
0015:19:08.4740;56.715;262.612;42.232;0;
0015:19:08.4770;56.715;262.152;42.224;0;
0015:19:08.4800;56.714;263.516;42.221;0;
0015:19:08.4830;56.713;264.762;42.224;0;
0015:19:08.4860;56.712;265.801;42.231;0;
0015:19:08.4890;56.712;267.596;42.242;0;
0015:19:08.4920;56.713;267.783;42.253;0;
0015:19:08.4950;56.714;265.995;42.260;0;
0015:19:08.4980;56.713;264.862;42.265;0;
0015:19:08.5010;56.711;263.663;42.269;0;
0015:19:08.5040;56.711;265.982;42.281;0;
0015:19:08.5070;56.709;268.076;42.297;0;
0015:19:08.5100;56.710;268.352;42.316;0;
0015:19:08.5130;56.709;266.863;42.334;0;
0015:19:08.5160;56.708;266.529;42.353;0;
0015:19:08.5190;56.707;268.573;42.376;0;
0015:19:08.5220;56.707;269.392;42.400;0;
0015:19:08.5250;56.706;269.079;42.423;0;
0015:19:08.5280;56.706;268.499;42.446;0;
0015:19:08.5310;56.706;268.128;42.470;0;
0015:19:08.5340;56.706;266.770;42.489;0;
0015:19:08.5370;56.706;267.370;42.509;0;
0015:19:08.5400;56.705;267.220;42.526;0;
0015:19:08.5430;56.706;267.439;42.541;0;
0015:19:08.5460;56.706;267.167;42.553;0;
0015:19:08.5490;56.705;266.222;42.561;0;
0015:19:08.5520;56.705;265.301;42.567;0;
0015:19:08.5550;56.706;265.268;42.570;0;
0015:19:08.5580;56.706;265.203;42.575;0;
0015:19:08.5610;56.706;265.004;42.578;0;
0015:19:08.5640;56.706;263.950;42.579;0;
0015:19:08.5670;56.707;264.080;42.576;0;
0015:19:08.5700;56.707;264.849;42.575;0;
0015:19:08.5730;56.708;264.230;42.569;0;
0015:19:08.5760;56.709;264.157;42.560;0;
0015:19:08.5790;56.710;263.813;42.548;0;
0015:19:08.5820;56.711;261.733;42.529;0;
0015:19:08.5850;56.712;260.149;42.510;0;
0015:19:08.5880;56.711;259.762;42.487;0;
0015:19:08.5910;56.711;260.726;42.466;0;
0015:19:08.5940;56.713;261.677;42.448;0;
0015:19:08.5970;56.714;261.388;42.427;0;
0015:19:08.6000;56.714;260.679;42.406;0;Datalogger trigger
0015:19:08.6030;0.000;0.000;0.000;0;
0015:19:08.6060;0.000;0.000;0.000;0;
0015:19:08.6090;0.000;0.000;0.000;0;
0015:19:08.6120;0.000;0.000;0.000;0;
0015:19:08.6150;0.000;0.000;0.000;0;
0015:19:08.6180;0.000;0.000;0.000;0;
0015:19:08.6210;0.000;0.000;0.000;0;
0015:19:08.6240;0.000;0.000;0.000;0;
0015:19:08.6270;0.000;0.000;0.000;0;
0015:19:08.6300;0.000;0.000;0.000;0;
0015:19:08.6330;0.000;0.000;0.000;0;
0015:19:08.6360;0.000;0.000;0.000;0;
0015:19:08.6390;0.000;0.000;0.000;0;
0015:19:08.6420;0.000;0.000;0.000;0;
0015:19:08.6450;0.000;0.000;0.000;0;
0015:19:08.6480;0.000;0.000;0.000;0;
0015:19:08.6510;0.000;0.000;0.000;0;
0015:19:08.6540;0.000;0.000;0.000;0;
0015:19:08.6570;0.000;0.000;0.000;0;
0015:19:08.6600;0.000;0.000;0.000;0;
0015:19:08.6630;0.000;0.000;0.000;0;
0015:19:08.6660;0.000;0.000;0.000;0;
0015:19:08.6690;0.000;0.000;0.000;0;
0015:19:08.6720;0.000;0.000;0.000;0;
0015:19:08.6750;0.000;0.000;0.000;0;
by Flavio Mussolin

You have the answer: "Drive system running for over 5 years without any problems".
The reduced mode for ID run IMHO is not the cause of the fault.
Complete ID run guarantee best performance for the drive, this depend on your application
by mvalente Rank: 5704 on 8/5/2017 10:30:46 AM | Like (0) | Report
This issue started about a week ago and initially it was a comm fault (7510) since it is controlled by a PLC in a ControlNet network.
After replacing all network components and eventually the drive itself, we changed the control over digital and analog inputs.
Then we started having OverFreq faults.
The drive runs fine for several hours (up to 8 hours) then it faults.
Sometimes it faults after just 20 minutes of run time and even faults when it is not running at all.
We have quite some people from ABB looking into this (they suggested a grounding issue but everything tested OK) but so far no solution.
Thanks for the comments!
Add new comment