Profibus new Slave configuration in a existing bus,station to upgrade the old one.
Sir, We have AC450 PLC with CI541 card. In bus 5 station 7 FIFE make edge guiding system was configured. Now we want to change the same with a double camera edge guiding system of same FIFE make. Previously for that PBS 10 with linked PBSD5 was configured. Now as per GSD parameter in PBSD5 I want to change the UPRMDLEN 0 UPRMData Blank to UPRMDLEN 3 UPRMData C00000. But while entering these parameters message was coming as cant configured as space is not available/ redim the element. So when I view the PBSD5 only UPRMDLEN 3 was showing where as the UPRMData showing nothing.
So what to do now.
I want to configure new PBS & PBSD then what to do.
Please respond..
Regards
Sailendu das
sailendudas@gmail.com
Answers
Redimension the controller data base. Dimension for more PBSD:s than you actually need. Note that there is also a limitation regarding the sum of UPRMDLEN and CFGDLEN (217 bytes).