I found an answer of similar question showing that it is not possible to use PU410K01 kit with 800xA ver. 4.1
Do you know if there available on market, possible as spare part, PU410 unit for 800xA ver. 4.1 or the only possible way is PCI - RTA board in the PC?
PU410 unit (also via POL or spare part) available for 800xA ver. 4.1 or only PCI RTA board is a solution for this version?
Voted best answer
Hello,
as far as I know, the PU410 was released for 800xA 5.0, with a separate installation package. In 5.1 the installation package is included with the other 800xA installation packages.
/Ronny
Answers
As Ronny wrote, the PU410 driver is available for 5.0 and 5.1.
In older versions you must use the PU515 (5 volt) or PU515A (3.3 and 5.0 volt) PCI-based RTA cards.
/Stefan