Any one have AC800M Diagnostic Library afw file/code for list Controller & S800 IO alarm in customized alarm list
Can any one help me getting AC800M Diagnostic Library afw file or code to know the detail of alarm as same to system status viewer. Because in the Project we have seperate alarm list for each area where is any Controller/IO is fault that alarm need to be generated with detail of the fault (Eg, Battary Low, Primary Controller Down, CN1 failure, Under flow etc..)
If this is included any special library pls lets uk know the point of contact.
Voted best answer
Which System Version are you using?
If you are on 5.1 FP4 and above, try using AC800M Status Monitoring.
This will not only let you know the status of Controller and its hardware but also provides direct navigation from IO channel to the faceplate of signal connected to it.