Dear Firends
I have ABB DCS system with remote IO(connected by profibus to AC800 Controller PM866).I have added one Siemens remote IO (ET200M,with IM153-1 interface card) to same profibus of ABB as a node and also I imported GSD file of this ET200M to ABB control builder.Now I added hardware of ET200M in control builder,but I cannot be online with that, and i get error of (Configuration Data fault) in ststus of ET200M board.Can somebody help me.what is problem and how should I config ET200M parameters.I have attached sonme pictures that shows error and ET200M hardware config in control builder.
thanks a lot.
Answers
"Configuration Data Fault" usually means whatever you configured in CBM does not match what you physically have installed in the field.
Your CBM hardware tree must match EXACTLY the ET200 hardware configuration.