Alarm updation on Alarm Line & Alarm list for AC400 connectivity in 800xA
Hi,
I have a below setup,
1. System version 5.0 Sp2
2. 1 out of 2 Aspect server.
3. 1 out of 2 connectivity server (AC400 Connect )
4. One no. of AC450 controller.
Recently, Both Aspect server's HDD's crashed, with Manitanence backup the system was Restored / Recovered fully in a New HDD's.
Issue 1:
The Alarms getting generated, but were not updating / appearing in the Alarm line & Alarm list. However, the alarms appear in faceplates & getting acknowledged.
How to resolve ?
Issue 2 :
When going for a Manitenance backup, the backup is getting completed with error for Aspect Object.
How to resolve ?
Answers
There are too many unknowns so I recommend contacting your regional ABB support center.
- Lack of alarms: check Event Collector service group for MB300. If custom Event Treats (alarm texts) is in use you must reload their definitions in RTA Board config.
- Error in backup: check backup log. Examine erroneous aspects. Repair corrupt/broken aspects, possibly with consistency checker tool. Install missing system extensions, etc
/S