IM aspect -> Error Connection to Server other node except local
Hi,
Could anyone help me.
I've installed 800xA sv5.1RevC (x64) sytem with two IMS (IM1 & IM2). Everything is fine for IM2 except for IM1 aspect accessing from every remote node.
I have error following error: Error Connection to Server.
note: IM1 aspect accessing is fine from localhost=IM1
What is wrong in my IM1 installation ?
thanks
Answers
Firewall config not complete in IM1?
IP address of IM1 bad in remote nodes' hosts files? Can you ping IM1 from remote nodes? -> use RNRP Config tool to refresh the files.
Web proxy setting wrong? Internal addresses should be excempted from proxy.
/Stefan
Hi Stephan,
IM1 has 2 network cards, when the 2th one is enabled, I had this error for aspect accessing from other node's plant explorer as showed in attached image.
When this card is disables everything is fine.
Thanks
Hi stefan,
The second network card is used for other 800xA Communincation (Third part Client/Server apllication)
The bind order of two cards is correct First=800xA Communication, Second=Third part communication
Thanks.