Why does AC900F have a fatal errror when downloading incremental changes via "Load Changed Objects"?
During hot commissioning, incremental downloads trip the process, and are causing delays.
When loading small changes, using “Load changed objects” the Controller percentage download progress window in CBF “freezes”.
When we look on the AC900F faceplate we get a Fatal Error message.
Voted best answer
Hello LJohnson1
the Fatal Error 10001126 as seen in the display is a know (and fixed) issue with Freelance 2016SP1. It happens under certain circumstances, when the number of objects to be incremental downloaded exceeds a certain limit.
You can download the Freelance 2016SP1 RU01 from MyControlSystem, provided you have a valid Sentinel agreement.