Redundant Server - Compact HMI
Hi,
Is possible configure a redundant server for Compact HMI 6.0? If not possible, what option could you use to implement some type of redundancy?
Answers
CHMI does not support redundancy.
Please go through the below link.
http://72.52.243.203/CHMI-xA-q870630.aspx
There are many questions answered on this in AKS. Please have a search.
CHMI does not support redundancy, however you can put 2 Servers in Parallel configuration as independent server.
Compact HMI supports an autonomous redundancy scheme.
This means that two Compact HMI systems are running in parallel accessing the same controllers. One of the systems are considered to be the main system and the second is the backup system. All configuration changes should be done in the main system and then transferred to the backup system by using the system backup function.
For more information on how autonomous redundancy configuration is done, refer the attached manual, pg: 152.
This means that two Compact HMI systems are running in parallel accessing the same controllers. One of the systems are considered to be the main system and the second is the backup system. All configuration changes should be done in the main system and then transferred to the backup system by using the system backup function.
For more information on how autonomous redundancy configuration is done, refer the attached manual, pg: 152.