Good day!
We have 800xA SV 4, redundant PM865 controllers with SM810. Sometimes we facing with an unexpected controllers shoutdown and memory reset. Battery was replaced lately.
In CI log file i found:
I 2017-07-05 12:42:01.932 (EHTask)[ERRORHANDLER] Send ErrorReport to PM. ('Modulebus: Scan time error', Sev = 4, ActionsToTake = 0xf)
E 2017-07-05 12:42:01.952 (EHTask)[ERRORHANDLER] ErrorReport not sent to PM. STATUS = 68616200
I 2017-07-05 12:42:01.952 (EHTask)[COMPONENTMGR] Component ERRORHANDLER report state PENDING_STOP
I 2017-07-05 12:42:01.952 (CompMgr)[COMPONENTMGR] External stall timer invalidated
I 2017-07-05 12:42:01.964 (INTERRUPT)[LATENCYSUP] Timeout on task. ConnId:10, Cycle:200, Lat-per.:20, TaskId:2
I 2017-07-05 12:42:01.964 (INTERRUPT)[LATENCYSUP] Last wd start came from normal tick.
I 2017-07-05 12:42:02.052 (EHTask)[COMPONENTMGR] Component ERRORHANDLER report state PENDING_STOP
I 2017-07-05 12:42:02.152 (EHTask)[ERRORHANDLER] ErrorHandler stopped SM since SSP failed
F 2017-07-05 12:42:02.152 (EHTask)[SM810FWROOT] FATAL ERROR in .\ErrorHandlerImp.cpp[564]: 0x8000
And in CPU log:
This PM has been intentionally stopped.
Reason:
- CPU stall timer has expired (Acknowledged)
- Memory parity error at address: 0x00000071
Press init button or remove power to restart...
_____________________________________________________________________________
0
Stalltimer is enabled with time = 1984 us
This is Lower CPU running as Primary CPU.
hing interface lo0...done
Please help me! What may be the reason of this behaivor?
Thanks in advance
Answers
Hi Denis,
I don't know if you already solved your problem but looks like you have some problem with your IO. Your log report a problem with a modulebus scan what is pretty common and can fixed chaging the scan time on cpu properties editor. What is really strange is that communication problem between cpu and SM810. You can try exchanging the SM810 and changing the cpu configuration to single as this configuration with Redundant HI controller is quite sofisticated...
Clayton
Add new comment