Our System has 2 ACS servers and 4 clients (Workgroup). There are two network switches configured as 172.16.4.X and 172.17.4.X. When 172.16.4.1 is disabled, PPA goes down. 172.17.4.1 is not taking up the network.
Also if i open RNRP, only 172.16.4.X series IP's are listed. Why 172.17.4.X IP's are not showing..But im able to ping all machines through both series IP's.
How can i make Sure of network redundancy?
If 172.16.4.X series switch is disabled, PPA should be up through 172.17.4.X. But that is not happening
SARGURU.G
Voted best answer
Hi,
A Network Adapter in a PC must never be "Disabled".If it is disabled the network redundancy function is lost. RNRP cannot update the IP routing table when the network adapter is disabled.
So,please check the redundancy by disconnecting the cable.
Refer 3BSE034463-510_A_en_System_800xA_5.1_Network_Configuration.pdf for more details.