How to Clean Database from Melody config Server in 800Xa system ?
Actually we want clean database in Melody config server.When we are opening the control structure it is showing 8699 tag but It is showing 28408 objects in melody object list.(find the attachment)
So anyone help us to delete database or delete the objects with bulk data manager.
Manually we are not able to delete objects from control structure.When we try to delete one pop up is showing that deletion of object shall be done only in composer only.
Thanks
Voted best answer
Answers
You can delete the objects or Tags which you don't need in your system or in your control structure. To do so, you can open ObjectList from your Melody Config server. search for that object type and delete.
There is a limitation, bulk delete is not supported. So you have to delete one after another.
Find the attachment, how you delete tag from ObjectList.
Hello Debashish,
But i want to delete and recreate the database.we have 29000 melody object in our system and we would not want to delete one by one.
I would strongly recommend to use the composer for all melody tags! Why do you want to clean up the database or to delete tags manually?
However, it is possible to get rid of tags by switch of the Validation of Melody Connect. But messing around in this way may lead to inconsistencies.
by nomakop1 Rank: 1862 on 6/20/2014 4:10:36 AM | Like (0) | Report
On config server there is a melody tag importer file called MelConverter.exe. When is melody tag importer off then double click on this file. Small window will popup. Then click on tools and there you can choose from 3 options. Hope it helps.
by nomakop1 Rank: 1862 on 6/20/2014 4:14:31 AM | Like (0) | Report
On config server there is a file called MelConverter.exe. When is tag importer off you can double click on it. Small window will popup. Then choose tools and you have 3 options. Hope it helps. :-)