OPC DA Client communication is not working correctly between 800xA and Freelance
I' ve 800xA system and ı want to communicate with other plant with using OPC communication protocol .I've changed some DCOM settings according to the "System 800xA Configuration 5.1" manuel. I tested with KEP server in order to sure the other system and it's working clearly. But I've tried with OPC test client and I couldn't read the other system. Can anyone suggest any solution or inform about DCOM setting?
Have a good work.
Answers
Hello,
To get the data of Freelance in 800xA ,we need a software called "800xA for Freelance", which get installed in 800xA nodes.And also, Freelance OPC also need to be installed in connectivity server to get the data of "Freelance" in 800xA.Configuration of aspect and connectivity server and also OPC gateway are required on Freelance CBF machine as well.
3Party OPC client can also be used to view the data of Freelance in 800xA but configuration on Freelance CBF machine and installation of Freelance OPC in cnnectivity is still required.
Hope this will answer your question.
Thanks and Regards