profibus FI 830 ,state: red, error: 29000005,kindly povide solution
Chamera Power Station
NHPC Limited
Answers
Hello,
If It's running plant situation then, I strongly recommend to get connect with local ABB colleagues for support. Find India ABB contact center detail @ http://www.abb.com/cawp/inabb506/9e084739681d443865257a1500422fea.aspx
Mean time if you can access controller webserver, dump controller log and attach here. At which phase this error appears while commissioning, normal plant run or while troubleshooting phase ?
Check few things,
-FI 830F module is is lock and mounted properly.
-Correct firmware is loaded to FI 830F.
-Controller Configuration is matching with physical hw and loaded to controller.
-there is no loose profibus cable connections. and profibus cables are correct.
-If it's redundant controller configuration then check profibus cabling in AC 800F M & I document.
-In CBF commissioning mode what is observation in hw tree ? FI830 status ?
more information will help in resolving the issue.