Alarm Expressions Bad/Good Qulaity Alarms in Alarm List
Hi
I want to remove the Good and Bad Qulaity Alarms from the Alarm List. I created the Object in Object Type Structe which have 1 Alarm Expression with 10 Expressions which will create 10 Alarms on Different expressions.
when 800xA System Lost Communication with Third Party Server. I get Alarm in alarm list with Bad Quality Data Recieve for each expression in the Alarm List and same happend when i get Communication back i get Alarm in the Alarm List Good Quality Data Recieve.I have instantianted 500 times in the Control Strucutre. So i get 500*10=5000 Alarms on each start or stop. which mess the whole alarm system.
I want to get rid of this Good and Bad Quality Alarms in the Alarm List
NOTE : I tired "BadQaulityEventProperties" General Property on SoftAlarms Level. and declare NotifyBadQulaityEvent=False and Grace Period as it mentioned in ABB Docuement-3BDS011222-510 Page 127. then restart the SoftAlarms Service
But still i am getting Bad/Good Qulaity Alarms.
Any idea how i can get rid ????
Voted best answer
I just tested in my lab using 5.1 FP4RevD and it did stop complaining over bad quality when setting NotifyBadQualityEvent to FALSE and restarting SoftAlarm service (all providers in parallel from service top level)
I suggest that you contact your regional ABB support center and ask for help.
/Stefan