Using the Totalizer in the dual loop CM30
Greetings
I do has an application with the dual loop CM30 controller
I do use two analog inputs , each had been scaled to represents the process value
I do want to do totalizing and monitoring of the two scaled signals , I did not mange to make the totalizer to increment by following the controller manual description
Kindly advice
Regards
Voted best answer
Hello,
I am not an expert on CM30, trying to help you out.
there are 3-4 possibilities of totalizing via digital i/p, pulse, fre and analog. Incase you want to totalize value via integrating against analog value, make sure that you have selected corrected mode and source.
The analog i/p unit should be set accordingly, check count rate and cutoff value if count rate is not properly set might be you don't get totaliser incremented as well if cutoff value set so high that totalizer stop counting. Check page 49-51 @
Hope that helps
Add new comment