Problem loading RTDB with ABB 800xA PLC Connect
Hello,
At the moment I am having problems with some of my Connectivity Servers. They used to be connected with an OPC Factory Server (Schneider), but now the connection is not working anymore. All the services in the service structure are ok, but when I do a deploy on my PLC Generic Control Network it says the Deploy Failed after loading the RTDB. When I look in my Log Files it says:
2012-10-31 16:15:47.131 MESSAGE 1440 (CS) RTDB Open CommServer (00000000) Deploy Id:{00000000-0000-0000-0000-000000000000} Version:132.20.146
2012-10-31 16:15:47.213 ***ERROR 01D8 (AE) LoadQuickstartFile C:\OperateITData\AdsServer\Generic Control Network Data {4AEDAF17-BAB3-4357-B65C-D31C14D1A2F0}\qsfrta.dat failed(80070002)
Does this look familiar for anyone of you?
Answers
Hello,
It seems there is a problem in the PLC Server Service. Restarting the service will fix this issue.
Go to service structure-- >PLC Server --> service Provider-- > Service provider definition. Uncheck the Enabled and apply and Check the Enabled and then Apply.
This will restart the service. And try to deploy.
If this does't work try to reconfigure the serve as below,