Could the CM30 used to contoler Weighting conveyor
Greetings
I d need to use the CM30 as a weighting conveyor controller to calculate both the flow rate and the total
I do receive two signals , the load cell feedback and the speed encoder feed back
could it be done by the CM30
can anyone help with an adea
have any one do such application with any other type of controllers
kindly advice
Regards
Voted best answer
Hi,
The CM30 can perform Math funcionality and also has totalizer funcionaity which means it is capable of measuring flow. However, the question here is while it most likely would be able to perform the mentioned application. I would need to know in detail what the equations you are using and more detail regarding the application before I can state with 100% certainty.
Regards
Niki
Answers
Niki
Best Regards
notes that the flow measurment equation shall be the follwoing
Q=(W*R)/L
Q is the flow rate (Kg/ min)
W is the weight of material on section of length L
R is the conveyor speed in m/min
L is the length of weighing platform in m
kindly Advice
Thanks in advance
Looking at the equation provided. Yes with a CM30 that has extended functionality we can cetainly perform that calculation and therfore use the product in his application. we can even customize the display to allow all variables to be displayed individually as well as the final calculation result.
Regards
Niki
Niki
Many thanks for your fast feedback
Regards
Good day
I do check the CM15 to do the same application
I think it could do the calculated equation /totalizing
is that correct?
kindly advice
Add new comment