Hi Stefan,
We have upgraded xA5.0sp2 with Plc connect and ac800m Pms lib to xA 6.0.2.
In the following order
1.upgraded the xA5.0 sp2 to xA 5.1 to convert vb to pg2.
2.created the production system for 6.0.2 and restored the backup and extended the nodes.
Here as per manual engineering base service should gets deleted automatically by system update but here engineering base service still exists in service str with undefined state as I know engineering base becomes oblete after 5.0,
How to clear that service from service str
Answers
If removing the service is the only task, just delete it like any object.
If root cause analysis is desired, then we need to backtrack and see where it breaks. I can't tell when/how this service is obsoleted, in pre 5.1 it was dependent on a MS SQL Desktop DB. If EB Service is to be deleted in version 6, it should be part of some post upgrade procedure.
Did you go through all upgrade instructions?
Seems like you forgot to complete the post upgrade procedure when upgrading from 5.0 to 5.1