800xA sv 6.0 Primary Aspect Server + CLS Failure
Greetings,
On a client's 800xA version 6.0 the system has:
1 x redundant Aspect/Connectivity Server (CTACS1 and CTACS2). The Primary AS/CS (CTACS1) is also the License Server.
4 x clients (CTCL1 and CTCL2 connected, CTCL3, CTCL4 pending)
1 x Information Management Server (CTIMS).
Last week, the Primary Aspect Server (CTACS1) shutdown due to a hardware fatal failure and it's permanent out of service.
The system it's now working, temporaly license has being granted to the other nodes of the system (CTACS2, CTCL1, CTCL2).
The 800xA sv6.0 system's console does not allow to install the function of CLS server to the redundant (CTACS2) server.
Any hits to install the CLS to the remaining AS/CS server without damaging the version 6 installation. It's well mentioned in the 800xA sv 6 user's manuals that from version 6 all the functions must be installed thorough the system console and its not allowed a manual installation because of lack of compatibility with the next updates of the system.
Do any one knows for how much time the 800xA sv 6 will allow operation of the plant until we replace the Primary Aspect/Server.
Thank you
Voted best answer
Expect license error pop-up window and unable to edit graphic/programs, there is no limitation for you to operate the plant without a permanent license
Add new comment