Aspect view wapper is not closing
I integrated a trend display with the aspect view wrapper in a graphic display.
When I open this screen with this integrated trend it seems that the trend will not be destroyed after a change of the screen.
When I navigate between two other screens, I always can see the trend display (I opened before) for a really short time. It seems that the trend display is still open in the background.
Answers
I made a very short attempt to reproduce this in 5.1 FP4RevD but I could not see any artifacts while changing display.
Are you using the Charts -> Trend control or the Special -> Aspect View Wrapper?
The sooner is recommended due to less overhead while the latter (aspect view wrapper) exists due to backward compatibility reasons, the latter has more overhead since you are really creating "a graphic display" inside "a graphic display" = 2x displays.
Can you share some more details?
/S
by Stefan Stromqvist
What version, service pack, rollup, TC do you observe this with?
by lukas_b Rank: 53 on 5/16/2014 6:02:22 AM | Like (0) | Report
SV5.1 FP 4
by lukas_b Rank: 53 on 5/16/2014 6:06:13 AM | Like (0) | Report
TC8a
by Stefan Stromqvist
Will check next week
Add new comment