how can i confirm the application in my laptop is the latest application which is running in ABB AC800M controller
Software Information: Compact Control Builder AC 800M, version 5.0.2/0 (Build 5.0.2004.52) System Version 5.0 SP2
Kindly can you confirm the below procedure is correct to verify the application in the laptop is the same application running in the controller
1- Open application in compact control builder
2- Go to Tool menu and select online.
3- Select the controller
4- Click continue
After some time i saw message at the bottom "You are onlie" and the header of the compact control builder is change to offline to Online. Is this means the application in the laptop is the same as the controller?
In the online mode i saw different icon on the hardware folder. Can you tell me what is the meaning of these icons. I have attched the snapshoot for your reference.
by SG Rank: 36 on 5/7/2014 11:19:52 AM | Like (0) | Report
Hi,
The procedure you said for going online is correct. If there is a mismatch between application on your server and controller, then you will not be able to go online without downloading the new application to controller.
The icons which you have highlighted is the configuration part of controller. Ethernet 1 and Ethernet 2 contains IP address and subnet mask of your primary and secondary network
If you modbus CI853, you will find it under com. If you are using module bus i.e modules connected on right side of controller or through cluster modules then it comes under module bus..CF Reader indicates flash card used in your controller for application storage.
Yellow colour indicates warning on Hardware status. Some of them can be cleared by pressing the clear latch button in hardware unit..
Its difficult to explain this basic things through this media. I request you to go through the manuals which will explain better..
Add new comment