800xA 5.0, PLC Connect, Generic Control Network Configuration
Hi,
I have PLC Generic Control Network in the system. I changed node where OPC server for PLC connection was installed and when I trying to change Adapter Data Source Service Group or Data Source Service Group it always revert to the last name. And i can't to deploy my network because "No contact with the server". Is it possible to change OPC server node?
Voted best answer
The OPC server should be in the same computer where you have PLC conectivity server created
Add new comment