What is Engineering base service?
This Particular service is down in my Aspect Connectivity Server (800xABase 5.1-PLC Connect). I tried to bring the service up by restarting the service and also by creating new service provider & service group..
How to bring this service up?
Voted best answer
The Engineering Service is only used if you are doing large scale system engineering with the complete installation of Engineering Studio.
In older systems it was installed by default. If you are not storing information like parameter manager, document manager etc in the Engineering SQL Database then you should delete the service and service group.
Answers
If I'm not remembering it wrong, Engineering Base is obsoleted in 5.1 (its shall be removed during upgrade to 5.1).
Have you imported the Service Structure from 5.0 into a 5.1 system?