One of our Client has a 800xA System with 5.1 Rev D Version commisioned around 8-9 Years back.
Recently they had ordered for some Spare Ci840 Modules. And CI840 spare modules with FW. Ver CI840 SW 4.3/1.
But when tested along with a already running CI840 at plant (Pair of Old CI840+ Newly supplied) its seen working well, without any faults during switching over from and redundacy and dual working fine. But a station warning with extended status (16#2020000) was observed in CBM Slave hwstatus. This is observed whenever the Old CI840 is in Prim Only , not during New CI840 is in Prim.
What could be the issue with this?
Answers
I've filled in the your extended status 2020000 (remove 16#) in the error code extract app and it shows device specific status 18 and not preferred version primary. You should upgrade the firmware of the old CI840 module.
by Harsha.D
Hope CI840 and CI840A not mixed and ensure both should be CI840A for proper switch working of redundancy
by akitapbayev Rank: 1348 on 12/22/2018 8:32:47 AM | Like (0) | Report
Hi, ABB experts! I have the same problem with CI840, at this moment firmware is 4.3/1 for both module (redundancy). And unit status in CBM shows: HWStatus is 16#00000002, Errors and warning status is 16#0202000, ExtendedStatus- 16#C0000000. All submodules hasn't any warning or alarms. Strange that another CI840 with same firmware hasn't any warnings. Could you help me to solve this problem? Or at least suggest in what way i should to figure out!
P.s.: I have checked profibus line and didn't found any problem, also downloaded firmware again. But no any effect.