800xA 5.1 FP4 Maintenance Backup Error
Hello Guys,
full Maintenance Backup is of my system ending up with couple of warnings and a error referring to some FF library objects, Backup is Auto scheduled via schedule structure.
we do not have any FF device in this project, so i do not understand why is this happening!!
the Error says -
"FFLibraries:FFUpload: En error occured. Return value hr=0x8000401a.
And
Warning is -
"As pect 'FFUpload' on object 'FFLibraries' failed to serialize itself.
Request your suggestion to get rid off this one.
Please find attached the Log report.
Thanks in advance.
Answers
Hello,
the error code means "The server process could not be started because the configured identity is incorrect. Check the username and password."
This is probably caused by the FFDataStorageAndDistribution service.
Have you changed your 800xA service password?
Please use the FF configuration tool to repeat the registration of the services. This should correct the password issue.
If you are absolutely sure you don't use Device Management FF, you could uninstall the DMFF system extension. But this requires several manual steps. ABB support can help you with this.
Best regards
Jürgen
Hello,
Due to interactive login applied to the FFDS folder, you have to keep the login user locked not to lockout from the Primary aspect server while running scheduled backups and if you want to take full backup take from the Primary aspect server only to get rid off errors.
Use Install user to take backup.