PLC Configuration Error
We are facing an ERROR with running our program after we login in to the PM564-T-ETH A0, this ERROR is “#151654426 E3: Int. PM5x1 ETHERNET PROJECT CONTAINS INVALID CONFIGURATION DATA”.
So we use another PLC PM564-TP-ETH A9 to run the same program without any change and everything run successfully. Please provide us with a solution to remove the error in the first PLC.
For your info:
- The version for the Control Builder Plus that we use is 2.2.0
- The nameplate for the 2 PLC’s can be attached from the above PDF file.
Answers
Hi
first, have you checked that the two units not have the same IP adress?
Without any change means that you have assign the same adress....
Hi
your conclusion is one good possibilities. My last test about the possibility to use T series give me in Automation Builder the follow result, with an alarm signal on the top
of screen
When I tried to use the TP series:
But I have Automation Builder 1.2 version, in Control Builder I not have the same possibilities to test
by alaa chabayta Rank: 2972 on 6/8/2017 4:31:52 AM | Like (0) | Report
hi Mr. flavio:
Thanks for ur help, the problem is from the plc firmware and we solve it,
the below video shows the solution:
https://www.youtube.com/watch?v=xIatoKXWSi8