soft controller with OPC
Hi all,
I have downloaded the application to Softcontroller and its working fine
when i checked the softcontroller logfile I found few network addresses
169.254.181.32:2,169.254.181.40:2,192.168.1.1:2 (LAN Card IP)
I have configured 192.168.1.1:2 in ABB controller system ID and ethernet address
in opc server when i try to connect 192.168.1.1:2 its showing error but available controller showing 169.254.181.32:2 and I am able to connect to this IP....
If i want to access from different PC i should have 192.168.1.1 IP :(
Any suggestion pls
Regards
sandeep
Answers
Change the Binding order on your Network adapters , then restart the soft contoller.
now opc is connected to soft controller application
from another Pc with 3rd party opc client is not detecting this
Please refer to 3BDS011222-510_F_en_System_800xA_5.1_Configuration Section "Accessing the 800xA OPC Servers" to configure third party OPC.
Add new comment