Smart Client Trend in graphic displayPG2 has stopped updating
I attached some pictures so you can see what i see. The Trend in the PG2 display does not show the same in smart client as it does in a workplace... It is just a straight line after a certain point. The straight line is three days long. It has been like this for a couple of weeks so the trend behind the three days seems to update like it is supposed to.
When you show a trend on the values in these tanks in smartclient (The value above the tank) the trend works and you see the correct trend but not in the display. It is not just display but several others aswell.
I have restarted the Smart Client server and all the Smart Client services on our IM server but the problem remains. Anybody have any other ideas?
Thanks in advance!
/Trinity
Answers
Hi!
Are you using hierarchical logs?
Could it be that 800xA Trend use "seamless" function to display data from all of the history logs and SC does not? (The SC Trend points to the first log only)
BR
Source: Smart CLient