Difference between S100 & S800 DI cards in Load Calculations?
In calculations of CPU load given forms in AC450/AC410 Manuals, in DI case the given execution time value is for the whole board (ex: AC450_DI 0.2 ms/board), then have to divide the result on the number of channels in board, that valid for S100 & S800 I/Os
So, i have S100 DI cards (32 channel) & S800 DI cards (16 channels)
Is that means that signal on S100 card consumes less load than signal on S800 card although they have same scan time and rate of change?
So, i have S100 DI cards (32 channel) & S800 DI cards (16 channels)
Is that means that signal on S100 card consumes less load than signal on S800 card although they have same scan time and rate of change?
Voted best answer
Yes! But are you surprised that central I/O is more efficient than distributed I/O?