The 800xA Device Manager and Asset Optimization work well througth 3er Party PLC?
Is possible Use the Device Manager (For Parameterization, Configuration and Diagnostic of Field Devices) and Asset Optimization for Asset Management of Field Devices Connected through 3 party PLC (specific Siemens and Rockwell)
My Client have an 800xA System with AC800M but also have 3 Party PLC Siemens and Rockwell and he want a unique tool for can make Asset Management of all Hart Field Devices of the Plant.
The 800xA Devices Manager can Read the DTMs of the Hard Field Devices through 3 Party PLCs?
The 800xA Asset Optimization functionalities for Field Devices work the same way that work with AC800M with 3 Party PLCs?
If that is possible somebody could refer to the ABB Document where that is explained?
Voted best answer
3BDD011934-510 Device management PROFIBUS HART configuration.
There is no way to get HART data directly from PLCs to 800xA.