AS like question(Please see the link as belows)
http://www402.abbext.com/Delayed-alarm-update-800xA-system-q6281118.aspx
We already check Time sync and RTA and Controller Setting.
And We attached System message as your advice.
Please, refet to attached file.
Thank you.
Answers
DCBAG 24 16 = MasterView table contain a not reachable RTA. Not fatal but should be corrected. Search AKS for how to use OMVT expert command.
DAXIxxx is PC interpreter error; will check and revert on that tomorrow (bank holiday in Sweden today).
Interpretation (and sources; documents available for download on ABB Library - user account required)
DAXI002 22 9 = Overload in PC-interpreter C
DAXI002 22 10 = Channel to MOTCON handler filled. Overload in system or an aborted handler.
Severity: HIGH
Source: ABB Master System Messages mtype 21, 22 and 132, 5766392-20
CXAA000 30 23 = Addressed DSD, MVI_DSD or TSD not found
Severity: LOW
Source: CX System Messages & Halt Error Codes, 3BSE000331/B
1) Please seek reason for overload reported by PC-interpreter C and resolve the cause for the overload.
2) Get DataSet, MVI or TextSet error corrected.
by Thomas Kruse Rank: 58 on 4/17/2017 10:10:03 PM | Like (0) | Report
The link does not work for me. Please add the necessary info to this question.