hello,
Check the following:
1.In CBF project, allocate a resorce ID for Process station(emulator).
2.Open interner explorer and open http://localhost:8888/ or http://127.0.0.1:8888/ or http://local machine IP address(this is the IP of your local machine):8888 and press enter.
3.If This page appears, write resorce ID in the box "Station no" which is mentioned in CBF project for Process station(Emulator) and initialize controller.**
4.Go to CBF project, Go online and check if "Version error" appears in front of your CBF project.
5.Download whole station for Process station (Emulator).
**If in step 3 , the specified page doesnt appear, then go to services(by writing services in RUN)->Freelance controller Emulator ->Start this service if stopped
Please revert if problem still exists...
Thanks
Answers
Hello,
Check in network configuration that emulator is configured on 127.0.0.1 ip address ? and allocated resource is running/started @ http://127.0.0.1:8888. pls reply back if not resolved.
Also recommend to go through getting started manual @ http://www05.abb.com/global/scot/scot296.nsf/veritydisplay/dccb84483ca27155c125
78da004a094c/$file/3bdd012560r05_en_freelance_9.2sp1_getting_started.pdf
and following threads on AKS
http://www402.abbext.com/Cannot-run-F...
http://www402.abbext.com/Emulator-c71... Hope that helps
Source:
The emulator only works when the PC has a network connection.
TCPIP cable to a switch is enough. The switch or hub needs no other network connection. When a ping to your own Ip-Adress is OK, the emulator can be startet.
first of all you have to choose the emulator during the installation