Freelance Trend Server and OPC server Freelance version 9.2
Is it possible to have OPC server and Trend Server in the same Computer??
I am with freelance version 9.2
If yes Please explain me how to configure OPC tunnel?
Answers
Yes you can use both in the same computer but you dont need to configure OPC tunnel at Dcom just fill as follow:
Tunnel Port: same port number at your OPC server. (9950)
DA Server: Freelance2000OPCServer.24 - this number (24) must be the ID that you used at your OPC-server Options (Configure)
AE Server:Freelance2000OPCAEServer.24 - this number (24) must be the ID that you used at your OPC-server Options (Configure)
Dear Csanchez,
It’s an interesting question.
It is recommended in getting started document 3BDD012560R0403 that "always to install and operate OPC Server and Trend Server on separate PCs."
Practically with available functionality it is not possible to run OPC and Trend server ( i.e. configure two gateways on same IP with different port in case of ABB OPC tunnel) on the same PC.
Hello! Here this document