IEC61850 OPC SERVER TO SCHNEIDER SEPAM S60 RELAY
Hi,
I am trying to communicate Schneider Sepam S60 Relays with our abb CET. For creating the scd file i am using IET CCT tool. What access point is used for schneider relays like for abb ref615 we use S1.
Thanks
Voted best answer
For Schneider, Siemens, A_Eberle relays, Access point name is P1
Answers
Access point names are defined in CID file for IED. Look for it there. Either it is S1 or P1.
Add new comment