AMM03 (Analog Master Module) to SPBRC410
Hiii All
Can we upgrade AMM03 (Analog Master Module) to SPBRC410, and how about the step procedure are same with upgarde MFP to BRC or any addition enggineering?
Thanks and regards
Voted best answer
Yes you can. But you will need to replace all ASM modules by ASI23. BRC410 does not support ASM. A good thing you will like is farewell to painful manual calibration. Some re-engineering is required since Function Codes used for ASI23 are changed, but is simple enough.
If you have INFI system in place (NPM, MMU), you just need to change NPM (and other controllers e.g. MFP on the same bus) setting to use Controlway instead of Modulebus. This will increase your bus speed/throughput a lot.
If you have older N90 system in place, suggest to contact local ABB sales/service to have a complete evolution assessment and plan.