Hello,
Is it possible to use the same pt100 on multiple AI835 analog input cards? If not, is it possible to take temp. compensation from the application using AI835, NOT AI835A, with which i think it is possible.
If none of the above is possible, is it possible to calculate it from the single pt100 inside the application and is it a good solution?
Thanks
Answers
It is not possible to use 1 Pt100 to more than one input or transmitter. That comes from measuring principle for Pt100 sensors.
Using of application value for temp. compensation is possible only for AI835A:
- Fix, the FJT is used as reference temperature -> there is an Output QW, where you can connect your value (described well in module help)
Last question is not clear - what do you want to calculate?