How to configure High speed Input and High speed Output in AC500 PLC?
Sir,
I want to configure High speed output counter (Pulse output , PMW).
Can you upload any DOC of refrance backup so I can understand concept?
Voted best answer
ABB has a good application example for step motion on the eCo PLC. It details how to use the High Speed Counter input, and High Speed Output. See link below.
Answers
Hello!
In codesys Help you can find a describtion on how to use fast counters.
This is the decribtion for the regular not the speciel CD522.
See attached PDF.
You just have to control the Control word and do a configuration in control builder+ or you can use th Function Blocks CNT_IO ONB_IO_CNT.
br
Gustav
by josh.donovan Rank: 143 on 3/25/2014 4:43:05 AM | Like (0) | Report
It depends on the hardware you are using. Are you using an eCo PLC?
by Nirav Rank: 703 on 3/25/2014 4:51:39 AM | Like (0) | Report
I can use any PLC AC500 series plc.
Yes I have eCo (554)also and if it required then I can also change CPU and can use additional IO module .