Hardware Error Code analysis
800xA System is reporting following two hardware fault messages. Repeating every 6-7 minutes. Looking for the explanation or the analysis of the hardware which is causing this messages.
Voted best answer
Is it a redundant configuration? It looks like there is a power supply problem since you are getting battery, RPA (redundant power A) and RPB (redundant power B) failure errors on both CPUs. For that reason I guess a switchover is taking place continuously.
Answers
Go online with CPU in Control Builder M.
Check hardware tree for indication and translation of error code(s).
Fetch & examine the controller logs with CBM -> Remote System dialog
Contact regional ABB support office if you need assistance with resolving the problem(s).
/Stefan
A tool to translate the errors. The 0 after the IP-address is the position of the HW-module that reports the error. Select correct module in the tool. In this case it is the CPU itself. http://www402.abbext.com/Login.aspx?GotoUrl=ErrorCodeExtract2_1-0_a712.aspx
Add new comment